f7ben Posted December 3, 2020 Share Posted December 3, 2020 1 minute ago, Big Crappie said: So putting a penny under a 20a fustat so it will work in a 15 amp socket is a bad idea? LOL Did that for years in the cabin but the wire was all 12 guage. Well if you needed 20 amps that’s one way to get it lol 1 Quote Link to comment Share on other sites More sharing options...
Big Crappie Posted December 3, 2020 Share Posted December 3, 2020 4 minutes ago, XCR1250 said: How much are they, I can let him know in case they send him the wrong 1. You have mail Quote Link to comment Share on other sites More sharing options...
Guest Posted December 3, 2020 Share Posted December 3, 2020 32 minutes ago, Frostynuts said: You were probably right on the breaker part, but not the higher part. The breaker is there to protect the cable. If you put in a higher fuse, and you have a problem, then there is a chance the cable becomes the fuse, and melts, and burns. If the fuse size that was there before was sized correctly and worked for many years, your best bet is to stay with the same size breaker that has done its job for many years previous. Do not up the breaker size, that is asking for trouble, and possibly a fire. Of course I agree about the HEAVIER breaker NOT being an answer. I just mentioned that almost jokingly, but in fact it was BASICALLY the right answer. My answer was tongue-in-cheek, because I do like these scenarios, and I do like XR. I get a kick out of these fixes, and wanted to chime in, out of fun. I turned-out being close. The negative response to my answer I construe as indicative of several members, who I have beaten on this site on a daily basis, and have a SERIOUSLY hard time, accepting that " OWNAGE, WITH POWER ". Quote Link to comment Share on other sites More sharing options...
Tinker Posted December 3, 2020 Share Posted December 3, 2020 So 2 pennies will run the stove ? 1 Quote Link to comment Share on other sites More sharing options...
f7ben Posted December 3, 2020 Share Posted December 3, 2020 1 hour ago, Polaris 550 said: Of course I agree about the HEAVIER breaker NOT being an answer. I just mentioned that almost jokingly, but in fact it was BASICALLY the right answer. My answer was tongue-in-cheek, because I do like these scenarios, and I do like XR. I get a kick out of these fixes, and wanted to chime in, out of fun. I turned-out being close. The negative response to my answer I construe as indicative of several members, who I have beaten on this site on a daily basis, and have a SERIOUSLY hard time, accepting that " OWNAGE, WITH POWER ". You’re a fucking moron Quote Link to comment Share on other sites More sharing options...
awful knawful Posted December 3, 2020 Share Posted December 3, 2020 2 hours ago, f7ben said: You’re a fucking moron He said basically 😂 Quote Link to comment Share on other sites More sharing options...
Guest Posted December 3, 2020 Share Posted December 3, 2020 4 hours ago, f7ben said: You’re a fucking moron And you're gay. I'd rather be a moron. Quote Link to comment Share on other sites More sharing options...
awful knawful Posted December 3, 2020 Share Posted December 3, 2020 4 minutes ago, Polaris 550 said: And you're gay. I'd rather be a moron. For ever Quote Link to comment Share on other sites More sharing options...
XCR1250 Posted December 10, 2020 Author Share Posted December 10, 2020 2 days ago he got the breaker and like Ben said that was what was wrong, he said this morning that the concrete floor had finally warmed up. 3 Quote Link to comment Share on other sites More sharing options...
smokin george Posted December 10, 2020 Share Posted December 10, 2020 8 minutes ago, XCR1250 said: 2 days ago he got the breaker and like Ben said that was what was wrong, he said this morning that the concrete floor had finally warmed up. We have stamped concrete in the main room and garage. Once we turn the heat on and it warms up it's easy to maintain the heat. Gotta love infloor heating 1 Quote Link to comment Share on other sites More sharing options...
smokin george Posted December 10, 2020 Share Posted December 10, 2020 We run a propane fired boiler for the infloor and a separate 40 gal elec hot water tank for water that's on a timer. The original owner had a big water tank that did both and the fkn thing chewed propane like a boss. Quote Link to comment Share on other sites More sharing options...
Guest Posted December 10, 2020 Share Posted December 10, 2020 On 12/2/2020 at 9:18 AM, Polaris 550 said: Circuit is tripping, can't handle the load. Need heavier wire or higher amp breaker. LOL! Come on X, ya' know I was close!!!! Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member Jimmy Snacks Posted December 10, 2020 Platinum Contributing Member Share Posted December 10, 2020 Our old Weil McClain finally shit the bed...new one going in tomorrow... Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member steve from amherst Posted December 10, 2020 Platinum Contributing Member Share Posted December 10, 2020 1 hour ago, Jimmy Snacks said: Our old Weil McClain finally shit the bed...new one going in tomorrow... What ya getting? Quote Link to comment Share on other sites More sharing options...
awful knawful Posted December 10, 2020 Share Posted December 10, 2020 Put a bigger breaker. I read on the net it'll fix it. Quote Link to comment Share on other sites More sharing options...
Voodoo Posted December 10, 2020 Share Posted December 10, 2020 24 minutes ago, awful knawful said: Put a bigger breaker. I read on the net it'll fix it. LOL. Breakers protect wire. I see stuff that makes me shiver. They do get weak over time. Easiest way to check is load it up, measure amp draw, infrared thermometer the breaker. It should not get much hotter than the environment it's in. If the draw is within %80 of the breaker and you see temps of 110F or more anywhere on the breaker, she's toast. I used to build boilers, dealt with thermolec. The up scaling of electric heat on demand used to be done with step controllers, with sensors that took outside temps, output temps and heat gain algorithms. It ain't rocket appliances if you understand how it all works. There is an 30 kw Make Up Air unit for a water treatment plant, SCR heating to maintain discharge air temperature I build, being tested at 600V under full load. We have since gone from the two speed motors with overloads to VFD's, controlled by the building PLC. The last ones, and maybe the last ever were for Toronto Community Housing. They needed an MAU to compensate for the air draw they had in the laundry room. As more and more dryers get used, my MAU ramps up the blower with a VFD and SCR heating to keep the room 70F with neutral air pressure. My best work ever IMO....too bad me and my dad are getting too old for this stuff. Our competition builds 3 year junk, we build 20 year units. 1 Quote Link to comment Share on other sites More sharing options...
awful knawful Posted December 10, 2020 Share Posted December 10, 2020 12 minutes ago, Voodoo said: LOL. Breakers protect wire. I see stuff that makes me shiver. They do get weak over time. Easiest way to check is load it up, measure amp draw, infrared thermometer the breaker. It should not get much hotter than the environment it's in. If the draw is within %80 of the breaker and you see temps of 110F or more anywhere on the breaker, she's toast. I used to build boilers, dealt with thermolec. The up scaling of electric heat on demand used to be done with step controllers, with sensors that took outside temps, output temps and heat gain algorithms. It ain't rocket appliances if you understand how it all works. There is an 30 kw Make Up Air unit for a water treatment plant, SCR heating to maintain discharge air temperature I build, being tested at 600V under full load. We have since gone from the two speed motors with overloads to VFD's, controlled by the building PLC. The last ones, and maybe the last ever were for Toronto Community Housing. They needed an MAU to compensate for the air draw they had in the laundry room. As more and more dryers get used, my MAU ramps up the blower with a VFD and SCR heating to keep the room 70F with neutral air pressure. My best work ever IMO....too bad me and my dad are getting too old for this stuff. Our competition builds 3 year junk, we build 20 year units. Backread in this thread. You'll see why I posted what I did. Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member Jimmy Snacks Posted December 10, 2020 Platinum Contributing Member Share Posted December 10, 2020 1 hour ago, steve from amherst said: What ya getting? I know this sounds stupid but I don’t know..since I’m a moron I called a guy that we have known for years and he is going to replace it for us and I didn’t ask what he ordered.😂 This one has a standing pilot and no damper so I do know the new one will have a damper and electronic ignition . Quote Link to comment Share on other sites More sharing options...
XCR1250 Posted December 10, 2020 Author Share Posted December 10, 2020 5 minutes ago, Jimmy Snacks said: I know this sounds stupid but I don’t know..since I’m a moron I called a guy that we have known for years and he is going to replace it for us and I didn’t ask what he ordered.😂 This one has a standing pilot and no damper so I do know the new one will have a damper and electronic ignition . Furnace? Boiler? Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member Jimmy Snacks Posted December 10, 2020 Platinum Contributing Member Share Posted December 10, 2020 (edited) 1 minute ago, XCR1250 said: Furnace? Boiler? Boiler Edited December 10, 2020 by Jimmy Snacks Quote Link to comment Share on other sites More sharing options...
XCR1250 Posted December 10, 2020 Author Share Posted December 10, 2020 2 minutes ago, Jimmy Snacks said: Boiler Ah. Quote Link to comment Share on other sites More sharing options...
Voodoo Posted December 10, 2020 Share Posted December 10, 2020 (edited) 49 minutes ago, awful knawful said: Backread in this thread. You'll see why I posted what I did. LOL I understand...and understood It is tripping the breaker, or blowing the fuse. Put a bigger one in... Like WTF, that is not what should be done, ever, by anyone... People some times ask me if I'm an electrician, I politely ask them not to insult me. My dad is an electrical and mechanical engineer. Schooled, certified. He can build a rocket ship on a napkin....give him a set of tools and ask him to assemble said rocket from his plans and he's fucked. Edited December 10, 2020 by Voodoo Quote Link to comment Share on other sites More sharing options...
snatchslayer Posted December 11, 2020 Share Posted December 11, 2020 I have a boiler on my ass 3 Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member Jimmy Snacks Posted December 12, 2020 Platinum Contributing Member Share Posted December 12, 2020 Apparently I bought a Made In The USA Utica Boiler.🇺🇸👍🏼 1 Quote Link to comment Share on other sites More sharing options...
Platinum Contributing Member Rigid1 Posted December 12, 2020 Platinum Contributing Member Share Posted December 12, 2020 14 minutes ago, Jimmy Snacks said: Apparently I bought a Made In The USA Utica Boiler.🇺🇸👍🏼 Manufactured about 30 miles from me.. Quote Link to comment Share on other sites More sharing options...