7 hours ago, AKIQPilot said:

Ok so things are pointing at a bad gas valve. Ben called it a few pages back. Hahaha. 

Im no expert but it seems everything is working like it should except the gas valve. 

For a more expert opinion you might try googling your model furnace and bad gas valve and see what you can find there. 

My thoughts from the beginning.

What he should do is call an HVAC service next time instead of jacking off not knowing what he's doing and looking for advice on the web, smh.

Link to comment
Share on other sites

8 hours ago, f7ben said:

The control circuit is probably all 24v ac and he isnt going to hurt anything with any modern meter checking around. 

Checking voltage is about as safe as you can get with a meter.

 

 

Link to comment
Share on other sites

25 minutes ago, snoughnut said:

My thoughts from the beginning.

What he should do is call an HVAC service next time instead of jacking off not knowing what he's doing and looking for advice on the web, smh.

Sounds like they got it though.  Coors Lights and gas, what could go wrong.:lol:

Link to comment
Share on other sites

32 minutes ago, snoughnut said:

My thoughts from the beginning.

What he should do is call an HVAC service next time instead of jacking off not knowing what he's doing and looking for advice on the web, smh.

^^^^^ This is exactly whats wrong with this country.......you're fucking idiotic attitude is why this country is filled with people that cant even change their own fucking oil. A bunch of know nothing pussies cause nobody gets their hands dirty

Thomas just learned about using a multimeter and a bunch about troubleshooting a simple electrical circuit and a bunch about how his and many furnaces work....he likely will be able to fix this himself for cheap and then help the next guy 

What you'd have him do is call some retard and pay that retard a shit ton to fix something simple......fucking idiot

Also if you thought gas valve from the beginning you are a fucking idiot because that is the least likely culprit in that circuit to go bad. 9 times out of 10 its the flame sensor or flow switch and then most of the rest of the time its a bad high temp limit. Rarely would a coil open up on a small solenoid valve like that

 

  • Like 1
Link to comment
Share on other sites

40 minutes ago, snoughnut said:

My thoughts from the beginning.

What he should do is call an HVAC service next time instead of jacking off not knowing what he's doing and looking for advice on the web, smh.

Why?  There is plenty of knowledge here that helped him trim down the list of possibilities.

However I would suggest not measuring a live circuit for resistance.  You can get both false readings, and possibly damage the meter.  All resistance/continuity testing should be done with the power off.

Neal

Edited by NaturallyAspirated
Link to comment
Share on other sites

9 hours ago, Tomas. said:

Hey guys. I am having an issue with my furnace and I am running out of ideas. The pilot light went out this morning and I have it lit again. The pilot light stays on but the main burners will not turn on. The induction motor runs. I changed the thermocouple but still no luck. Anyone have any ideas? It is a Nordyne M1GH 090A AW. 

Gas valve.

Link to comment
Share on other sites

2 minutes ago, NaturallyAspirated said:

Why?  There is plenty of knowledge here that helped him trim down the list of possibilities.

However I would suggest not measuring a live circuit for resistance.  You can get both false readings, and possibly damage the meter.  All resistance/continuity testing should be done with the power off.

Neal

You can trouble shoot switches in a 24v circuit like Tom had him do......not going to hurt anything and the specific resistance isnt important. 

The other issue with troubleshooting those switches via resistance when you dont really know what you are doing is you will read through the control transformer and may get confused sometimes. 

I prefer checking for voltage across switches in circuits or checking both sides to common etc. That is much more reliable 

Link to comment
Share on other sites

Just now, f7ben said:

You can trouble shoot switches in a 24v circuit like Tom had him do......not going to hurt anything and the specific resistance isnt important. 

The other issue with troubleshooting those switches via resistance when you dont really know what you are doing is you will read through the control transformer and may get confused sometimes. 

I prefer checking for voltage across switches in circuits or checking both sides to common etc. That is much more reliable 

Perhaps, it depends on the meter and how protected it is.

Voltage would have been a safer standard practice to check for.

Neal

Link to comment
Share on other sites

Tomas......disconnect the wires going to the gas valve and check the resistance of the coil. Should be some small amount of resistance there....a few ohms etc. If your meter reads a one you have an open coil although if the valve itself was clicking that is not likely. 

If its a sticking valve do what moto said. Beat its ass or just replace it :lol: 

Link to comment
Share on other sites

1 minute ago, NaturallyAspirated said:

Perhaps, it depends on the meter and how protected it is.

Voltage would have been a safer standard practice to check for.

Neal

I dont think they sell meters any more that would become damaged checking for ohms on low voltage circuits :lol: I have a couple cheap meters and have fed them 120/240v in ohms accidentally many times. My meters at work have seen 480v on ohms countless times by accident 

Link to comment
Share on other sites

49 minutes ago, snoughnut said:

My thoughts from the beginning.

What he should do is call an HVAC service next time instead of jacking off not knowing what he's doing and looking for advice on the web, smh.

The plumber makes a valid point.

12 minutes ago, f7ben said:

^^^^^ This is exactly whats wrong with this country.......you're fucking idiotic attitude is why this country is filled with people that cant even change their own fucking oil. A bunch of know nothing pussies cause nobody gets their hands dirty

Thomas just learned about using a multimeter and a bunch about troubleshooting a simple electrical circuit and a bunch about how his and many furnaces work....he likely will be able to fix this himself for cheap and then help the next guy 

What you'd have him do is call some retard and pay that retard a shit ton to fix something simple......fucking idiot

Also if you thought gas valve from the beginning you are a fucking idiot because that is the least likely culprit in that circuit to go bad. 9 times out of 10 its the flame sensor or flow switch and then most of the rest of the time its a bad high temp limit. Rarely would a coil open up on a small solenoid valve like that

 

People telling him to check for ohm's on a simple open or closed circuit :lol: 

Link to comment
Share on other sites

5 minutes ago, f7ben said:

You can trouble shoot switches in a 24v circuit like Tom had him do......not going to hurt anything and the specific resistance isnt important. 

The other issue with troubleshooting those switches via resistance when you dont really know what you are doing is you will read through the control transformer and may get confused sometimes. 

I prefer checking for voltage across switches in circuits or checking both sides to common etc. That is much more reliable 

Yup.

Link to comment
Share on other sites

Just now, NaturallyAspirated said:

@Tomas., Have you checked the voltage across the ignitor/flame sensor?  If your ignitor has opened up everything will check out, and if the solenoid on the gas valve is ticking it could be that.  Looks like a small black carbon spiral.

Neal

He said he replaced the flame sensor and that his pilot is lighting

Link to comment
Share on other sites

Just now, f7ben said:

I dont think they sell meters any more that would become damaged checking for ohms on low voltage circuits :lol: I have a couple cheap meters and have fed them 120/240v in ohms accidentally many times. My meters at work have seen 480v on ohms countless times by accident 

Perhaps.  I blew up a self built kit meter in tech school measuing ohms on a live circuit.  :lol:

Neal

Link to comment
Share on other sites

Just now, Mileage Psycho said:

The plumber makes a valid point.

People telling him to check for ohm's on a simple open or closed circuit :lol: 

Well would you send him to fucking tech school for two years to try and learn how to do what he did? It aint rocket science.  The plumber made no point at all......fuck calling someone for every little thing that goes wrong. 

Link to comment
Share on other sites

Just now, NaturallyAspirated said:

Perhaps.  I blew up a self built kit meter in tech school measuing ohms on a live circuit.  :lol:

Neal

We should just make sure that Tomas who is more comfortable with his meter now knows to never put the leads where the lightbulb plugs in :lol: 

Link to comment
Share on other sites

2 minutes ago, f7ben said:

Well would you send him to fucking tech school for two years to try and learn how to do what he did? It aint rocket science.  The plumber made no point at all......fuck calling someone for every little thing that goes wrong. 

Had to replace my furnace fan capacitor a few weeks ago. Would have cost me $100 for a service call. I did it for $25. 

  • Like 1
Link to comment
Share on other sites

21 minutes ago, f7ben said:

^^^^^ This is exactly whats wrong with this country.......you're fucking idiotic attitude is why this country is filled with people that cant even change their own fucking oil. A bunch of know nothing pussies cause nobody gets their hands dirty

Thomas just learned about using a multimeter and a bunch about troubleshooting a simple electrical circuit and a bunch about how his and many furnaces work....he likely will be able to fix this himself for cheap and then help the next guy 

What you'd have him do is call some retard and pay that retard a shit ton to fix something simple......fucking idiot

Also if you thought gas valve from the beginning you are a fucking idiot because that is the least likely culprit in that circuit to go bad. 9 times out of 10 its the flame sensor or flow switch and then most of the rest of the time its a bad high temp limit. Rarely would a coil open up on a small solenoid valve like that

 

:fuckyou: complete idiot

20 minutes ago, f7ben said:

Did I mention you're a fucking moron Snonuts?

once again :fuckyou:

1 minute ago, motonoggin said:

Had to replace my furnace fan capacitor a few weeks ago. Would have cost me $100 for a service call. I did it for $25. 

Oh no, the fucking horror and being the socialist you are, even if you had called a service, you would have expected it for free.

Link to comment
Share on other sites

10 minutes ago, Mileage Psycho said:

The plumber makes a valid point.

People telling him to check for ohm's on a simple open or closed circuit :lol: 

You get it Vince but Bent is far too stupid, most people won't or do not want to mess with their own HVAC but Google changes all of that. :lmao:

Link to comment
Share on other sites

1 minute ago, snoughnut said:

:fuckyou: complete idiot

once again :fuckyou:

Oh no, the fucking horror and being the socialist you are, even if you had called a service, you would have expected it for free.

No, I wouldn't have, which is why I did it myself. :lol:

 

Link to comment
Share on other sites

Just now, snoughnut said:

You get it Vince but Bent is far too stupid, most people won't or do not want to mess with their own HVAC but Google changes all of that. :lmao:

I get both points.  Hopefully Thomas realized this forum probably isn't the best place to seek some advice.  Because OMG.  There are much better forums and sites to seek advice like this.  This place (and others) can turn into a full on clown shit show for technical advice.  Most would be better off grabbing a hammer and smashing whatever they are trying to fix to see if that works.

  • Haha 2
Link to comment
Share on other sites

1 minute ago, snoughnut said:

You get it Vince but Bent is far too stupid, most people won't or do not want to mess with their own HVAC but Google changes all of that. :lmao:

Lmao it's not like he's getting advice on installing a new heat exchanger or something. No one is going to die from replacing a bad sensor. Jesus. :lmao:

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Trying to pay the bills, lol

×
×
  • Create New...